I have a v3f16 kone drive/inverter that i sent to be repaired after getting fault 0026 followed by 0106, after installing it now, it only releases brakes and jumps up when we try to drive down.

Is there any installation or parameter change needed after installing it again? its the exact same one that we took down 1 week ago from this elevator. Would not expect it to not "just" work since nothing has changed exept repair, unless the repair company deleted some parameters?



   
Quote
(@nackaboi)
Active Member
Joined: 17 years ago
Posts: 6

   
ReplyQuote
(@jasonli)
Active Member
Joined: 17 years ago
Posts: 11

   
ReplyQuote
(@dunkdadrunk)
Active Member
Joined: 17 years ago
Posts: 12
 
you could also open it up and check the relays inside, i have had a similar problem and it was the brake signal from the drive was intermittently failing. i opened the drive up, cleaned the relays up, put it back together and voila, the car returned to normal service.



   
ReplyQuote
(@vadim)
Trusted Member
Joined: 17 years ago
Posts: 46
 
Reset the parameters to factory settings and set them again using the KONE instruction for kdl16l

And what about faults?

Last edited by Vadim; 08/28/25 06:02 PM.


   