IDEC izumi fa-2j junior PLC Controller

5 Posts
1 Users
0 Reactions
4,191 Views
(@shoemaker)
Joined: 1 second ago
Posts: 0
Topic starter   [#29464]
Hi ,

Need some Good ideas !!!!!

Controller: idec izumi fa-2j plc controller

Traction, 6 stop.... copenhagen😊😊

Problem:

In position normal the elevator Burns 2 of the 3
Main fuses on the 3 phases that goes into the
Elevator control room (machine room)

No problems in position Manuel on top of cabin !!!!
I Can drive the elevator up and Down in position slow
Speed .... ā€œthe danish monteur positionā€ !!!

Fuses Burns only when the High speed relay is activated
( in position ā€œ normalā€)

And i have replaced the High speed relay, but the elevator
Keeps on burning fuses

/shoemaker

Attachments
D3B94EC8-30C7-4D71-9870-9419212F2962.jpeg (2.35 MB, 25 downloads)
611F3290-A4A8-4A4F-AC44-2654A3C12B4D.jpeg (96.57 KB, 18 downloads)

Last edited by shoemaker; 06/16/20 05:23 PM.


   
Quote
(@Huskervator)
Joined: 1 second ago
Posts: 0
 
What kind of drive? Or, is this a 2-speed AC motor with high speed windings bad?



   
ReplyQuote
(@shoemaker)
Joined: 1 second ago
Posts: 0
Topic starter  
Hi Huskervator,

And thanks !!!!

It’s a 2 speed AC motor !!!!!

I took of all cables to the engine ( 2 X 3 phases from the PLC
CONTROLLER and i measured the windings
( between each one of Them both on High speed
Windings and slow speed windings and between Ground
And each phase terminal)......
It looked okay

Attachments
0D874410-81E9-4C88-B950-9D69AE5293CB.jpeg (2.56 MB, 14 downloads)
EC770B23-7400-4778-A3FD-743DB71BD953.jpeg (2.23 MB, 12 downloads)

Last edited by shoemaker; 06/16/20 06:09 PM.


   
ReplyQuote
(@ElevatorGuy128)
Joined: 1 second ago
Posts: 0
 
not too familiar with that type but wondering if you can disconnect the motor from the controller and then try running it on high speed... see if the fuses then pop without the motor connected, that'll at least either eliminate the motor as an issue or if it only pops with the motor connected then i would assume its related to the motor. again not familiar with this setup so im not even sure you can do that? either way interested in what you find so please keep us updated!



   
ReplyQuote
(@shoemaker)
Joined: 1 second ago
Posts: 0
Topic starter  
Hi Elevatorguy 128,

Just wanted to share back,that the engine Got new
Windings and it runs like a Dream 😊😊👍

/ shoemaker



   