Customer wants to change an I-3 to Maxton valve on a TAC-20 controller, any help appreciated. Jumper settings?



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
Just change valve type M12 from a 1 to a 4 and be prepared to change valve coil relays K1-K8 more often than normal. It's not that big of a deal, not like you will be constantly replacing relays but the Maxton coils have a lower resistance and are a little tougher on those little tiny Schrack relay contacts.



   
ReplyQuote
 Boa
(@boa)
Estimable Member
Joined: 17 years ago
Posts: 141

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@elevator17)
Active Member
Joined: 17 years ago
Posts: 3
 
I'm installing a ICON CONTROLLER with a maxton valve
and not sure if the US1 and US2 is the coil terminal
Any suggestions
Thanks



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@jimbonj)
Estimable Member
Joined: 17 years ago
Posts: 67

   
ReplyQuote