I-3 to Maxton Valve

7 Posts
1 Users
0 Reactions
8,386 Views
 Boa
(@Boa)
Joined: 1 second ago
Posts: 0
Topic starter   [#16959]
Customer wants to change an I-3 to Maxton valve on a TAC-20 controller, any help appreciated. Jumper settings?



   
Quote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
Just change valve type M12 from a 1 to a 4 and be prepared to change valve coil relays K1-K8 more often than normal. It's not that big of a deal, not like you will be constantly replacing relays but the Maxton coils have a lower resistance and are a little tougher on those little tiny Schrack relay contacts.



   
ReplyQuote
 Boa
(@Boa)
Joined: 1 second ago
Posts: 0
Topic starter  
Thanks. This will change to where it will use both coils for high speed?



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
Ya



   
ReplyQuote
(@elevator17)
Joined: 1 second ago
Posts: 0
 
I'm installing a ICON CONTROLLER with a maxton valve
and not sure if the US1 and US2 is the coil terminal
Any suggestions
Thanks



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
Yes it is, UP Slow



   
ReplyQuote
(@JimboNJ)
Joined: 1 second ago
Posts: 0
 
Maxton has a pretty good troubleshooting app for smartphones



   
ReplyQuote