25/07/2017 9:10 pm
Dear All,
Could you help, please?
Gen2 Regen stopped with error 713 Block by 208, the first problem happened did power supply reset then the lift ran normally for 3/4 days only. 208 error means a fault on the capacitors of DC link, but we can't find any problem on capacitors. Any an idea about this issue?
Thanks in advance
25/07/2017 10:19 pm
Check the batteries. Even if they read good they still need to be replaced every few years.
Topic starter
26/07/2017 1:59 am
Dear Jluff,
which battery do you mean?
Topic starter
27/07/2017 12:51 pm
Lift OK after changed the GDCB part number ACA26800KT1.
Thanks ALL
Thanks ALL
Topic starter
30/07/2017 1:40 pm
after 3 days working well, lift again shut down with the same the error " error 713 Block by 208 "
31/07/2017 12:00 am
Drive caps are getting weak. If you can source new, replace them. This is a known issue on newer drives, there is an upgraded drive available from Otis.
Topic starter
08/08/2017 8:16 pm
lift working well after replaced 3 contactors inside the drive