Elevator Forum

Dover oildraulic so...
 
Notifications
Clear all

Dover oildraulic solid state control

8 Posts
1 Users
0 Reactions
6,693 Views
(@Up and down)
Joined: 1 second ago
Posts: 0
Topic starter   [#18859]
1970s 4 stop, will not run down on auto will run up fine and will run up and down on inspect. I have tried new cards out of a running unit with same problem. Does anyone have a print of the logic circuits are any idea what to check.



   
Quote
(@Rolly)
Joined: 1 second ago
Posts: 0
 
If I remember correctly you can run those on inspect all the way down to the springs. Check the bottom limits. They stop from running down on auto.



   
ReplyQuote
 jkh
(@jkh)
Joined: 1 second ago
Posts: 0
 
Print numbers are posted in the controller. I may have what you need. Pm me that and an email address.



   
ReplyQuote
(@lowoil)
Joined: 1 second ago
Posts: 0
 
Check 1a and ta



   
ReplyQuote
(@Up and down)
Joined: 1 second ago
Posts: 0
Topic starter  
Page 1. 122864
Page 2. 122867
Page 6. 119005
Page 7 119322
Vmp. 119882

Jkh I sent you a pm but later said it failed so here it is.

[email protected]



   
ReplyQuote
(@Up and down)
Joined: 1 second ago
Posts: 0
Topic starter  
1a and ta are ok signal is getting to the card for a down call but dosnt pick checked everthing today we could think of and still nothing. Did they make a print that showed the logic side



   
ReplyQuote
(@lowoil)
Joined: 1 second ago
Posts: 0
 
Do u have at least 24v funny things can happen if too low



   
ReplyQuote
(@Up and down)
Joined: 1 second ago
Posts: 0
Topic starter  
Think it was putting out 31 volts but 1a and ta were 15.1 vdc



   