Dover hydro with Ibm relays.

7 Posts
5 Users
0 Reactions
4,052 Views
(@bigshow79)
Active Member
Joined: 17 years ago
Posts: 5

   
Quote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473

   
ReplyQuote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473
 
300VDC relative to what?? each other (answer above) referenced to negative on rectifier?? referenced to Positive on rectifier?? Do you have a door operator print??



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
 
I had this once on a DMC. . It was bad capacitor under door controller But it was intermittent

Last edited by Jluff; 12/26/21 12:29 PM.


   
ReplyQuote
(@slider)
Eminent Member
Joined: 17 years ago
Posts: 17

   
ReplyQuote
(@bigshow79)
Active Member
Joined: 17 years ago
Posts: 5
Topic starter  
Yes. I have a faded door operator prints. If i open the door with operator de energized. When its energized it will close it. Bad re



   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
I would look at the capacitors that are paralleled around the contacts on the open and close relays. One of them is most likely shorted.



   