Doors not opening with a hall call. Hall call latches but the doors will not reopen at the floor that the car is at with a hall call. SE, DO button, and car calls all work properly.



   
Quote
(@Montana)
Joined: 1 second ago
Posts: 0
Topic starter  
Any help would be much appreciated. Thanks so much.



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
Only when the car is already at the floor or for any hall call? Both directions or certain floors?



   
ReplyQuote
(@Montana)
Joined: 1 second ago
Posts: 0
Topic starter  
Only when the car is already at that floor. Up or down all floors.



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
This N/C 10A contact is my best guess. If that is the problem a car call at the floor would do the same thing.
Attachments
4FE52EFF-F671-4E7E-82E4-8E272A9C281A.jpeg (1.12 MB, 59 downloads)



   
ReplyQuote
(@Montana)
Joined: 1 second ago
Posts: 0
Topic starter  
Ok, I'll take a look at that first thing Monday morning. Thanks buddy.



   
ReplyQuote
(@Montana)
Joined: 1 second ago
Posts: 0
Topic starter  
10A#2 relay fixed the problem. Thanks so much for the help you guys, you helped me add 1.5 years onto my life, and saved me some hair. Haha.



   