Hi guys. Got a dmc1 that keeps trapping people inside.
It seems to be stopping a few inches above the floor in the down direction on the down terminal landing as well as the intermediate floor above it. It’s a 3 stop It stops , calls get cancelled and it shuts down. I didn’t have my computer on me but I will tomorrow morning. Does this sound the door zone reed switch ?



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
You’re saying it runs down and stops 3” above the destination floor? Sounds like a level down problem. I’ve seen exactly this on a DMC1A with a bad level down switch. Could be your level down sensor on selector but several relay contacts could cause this too. When the DMC hits the slowdown point it drops the RDM (run down) output and picks the LE (level enable) output so you are now relying on a different circuit to keep DN1 & DN2 picked until the car gets to the floor. To only happen in the down direction you would be looking at contacts on relays LU, LD, DZ, & HW3.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
Yes. It was traveling in the down direction, and stopped a few inches above the floor, calls dropped out, and car was shut down.



   