Hey guys, Recently had the CLC not working, it would turn On then right away off. Changed Power Supply and it started functioning properly, except the hall call circuit, which it would not hold the light. Car arrives but the light will be off the whole time. Happens at all hall stations. Checked fuses, “validate floor” parameter and car is the Master(Single 3stop). I also did 2 Hoistway setup. It does not happens in the car call, only hall up or down dont matter. Any suggestions?



   
Quote
(@Johnny)
Joined: 1 second ago
Posts: 0
 
Wrong common??? Is this a new job, or an older one?? Is there 24vdc between the commons at the hall stations??



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
The toggle switch in the COP



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
Hall call common is P24G so the buttons light and call the car but the CLC outputs that latch the calls are powered from P24GS. S for Switched, after the 3 pole toggle switch.



   