Notifications
Clear all
Topic starter
31/10/2017 6:05 am
33OA . Says on inspection . But all my inspection switches on car top, in car station and in machine room ring out ok and are in the run position. Changed CRIP board, changed CIOACD 3.Q. Checked I/O'S under status JREC (car top, Inactive = OK), (JRECC ,in car inspection inactive = ok) Drained GCIO 360 Capacitor 15 min, to .0070 vdc.
AND GO.......
THANKS
31/10/2017 7:02 am
I wonder if it would change if you disconnect the wires at the cpu?
31/10/2017 7:53 am
Last edited by Indirtwetrust; 10/30/17 11:55 PM.
31/10/2017 10:00 am
Replace GCIO
31/10/2017 11:21 am
On some equipment, car door/hall door bypass switch if turned on when the car is on auto will issue an INSP command. Confusing as heck if you're not ready for it.
Topic starter
01/11/2017 2:23 am
CHANGED ALL INSPECTION KEY SWITCHES AND CAR TOP INSPECTION ROCKER. STILL NOTHING.... ORDERED NEW SOFTWARE 3.61
WE WILL SEE...
Topic starter
02/11/2017 1:15 am
SOFTWARE CHANGE DID NOTHING. SAYING AT 3RD FLOOR.REALLY AT BASEMENT. ALL IN NORMAL POSITION. SAYS ON INS. 121X 6E FAULT. NEW SWITCH INSTALLED. STILL NOTHING...
Topic starter
02/11/2017 1:18 am
SAYS MISMATCH ON CAR TOP INSPECTION SWITCH . NEW SWITCH AND THE FAULT STILL IS THERE
04/11/2017 10:17 am
Replace GC10
23/05/2018 2:06 am
Replace CIO board inside the COP with the same version.
23/05/2018 6:15 am
GCIO
Topic starter
21/12/2018 8:42 pm
Thanks guys , I found a broken wire on the CIOACD . All better. !