Elevator Forum

1956 Otis relay log...
 
Notifications
Clear all

1956 Otis relay logic

20 Posts
8 Users
0 Reactions
23.2 K Views
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143

   
ReplyQuote
(@uppo72)
Honorable Member
Joined: 17 years ago
Posts: 562
 
Seem to remember that there was a plate on the controllers with the last rectifier reading, so as to keep tabs on the control voltage.



   
ReplyQuote
(@danzeitz)
Prominent Member
Joined: 17 years ago
Posts: 672
 
As those old rectifiers go bad the DC voltage drops and they start passing more AC that causes a bucking effect on your coils making it harder and harder for them to pick. On newer solid state controllers you will see it lock up or cause all inputs / outputs to fire. I learner a long time ago to take voltage readings AC and DC and write them down. So you may read 120VDC with 2VAC. Then when you start getting weird problems you have a base line to start from. But rectifiers and power supplies will drive you crazey till you get ahead of them and know what they read when everything was normal. Good Luck



   
ReplyQuote
(@patrcik)
Eminent Member
Joined: 17 years ago
Posts: 24
 
if you ever need parts for these old Otis units try Master Elevator Components, they have a lot of parts for the 1950's and before.
www.masterelevator.net



   
ReplyQuote
(@turbo6)
Estimable Member
Joined: 17 years ago
Posts: 118
 
I had a similar issue a few years back and it ended up being a bad interpole on motor. Maybe start checking your loop circuit.



   
ReplyQuote
Page 2 / 2
Share:
Scroll to Top