Kone machines can be so fickle sometimes. The lights on the cpu for 61:U, 61:N and 30 will actually go low when it has seen the magnet. I.E. when the ...

8 years ago
Reply

I'm assuming you probably did a LON download? It is accessed through menu 5-7-1. You wouldn't think the software versions would change just from getti...

8 years ago
Reply

GAL recently bought Courion as well (in Jan 2018). I wouldn't mind seeing GAL freight door integration. Something other than EMS or Peelle.

8 years ago
Reply

Be sure roll call parameter is set correctly. I can't remember which parameter it is.If I remember correctly there is a way to test the floor board co...

8 years ago
Reply

Yes please. My email is [email protected] I haven't had any issues with that MPH for over a month now. Kind of frustrating. Thanks

8 years ago
Reply

Is it possible the brake switch is bad? If not you may want to switch to a different input. Are you getting any other faults at the same time? If you ...

8 years ago
Reply

Thanks I will verify that next time I am in the building

8 years ago
Topic
8 years ago
Replies: 7
Views: 9487
Topic
Replies: 0
Views: 1878
Reply

NOTIME, could I get that print too? Thanks

8 years ago