According to Cetek ALU is a software input that is the sum of several inputs associated with door zone. The signal is only viewable from the tool, it ...

4 years ago
Reply

Operator switches have been replaced and all wiring checks out. Door open, door close and detector input wires have been lifted while failing and issu...

4 years ago
Reply

Tried two new I/O interface cards, problem remained. Replaced second input card and issue cleared immediately, which it sometimes would with a power c...

4 years ago
Reply

Swapped the input backplane and the first input card, input test now passes. Was also able, with assistance from Cetek, to initialize the non volatile...

4 years ago
Reply

Micro switches check out ok and have also been replaced. I poked around the tool a bit today and spoke with Cetek. We found that my ALU software input...

4 years ago
Topic
4 years ago
Replies: 13
Views: 10510
Reply

This was a problem on early GCS controllers. A software update resolved this issue as well as several other issues.

4 years ago
Reply

Relay type and nomenclature looks like a GAL controller I had on my route.

4 years ago
Reply

Originally Posted by Jluff Can you communicate to CLC Pretty funny

5 years ago
Reply

Originally Posted by ILikeElevs just boggles my mind every time i see someone having an issue with the $4600 DMC1 freedom ware tool or the 6k modul to...

5 years ago
Reply

Usually “SA”

5 years ago
Reply

I’m familiar with this forum, I find there is better traffic in this section and my post is more likely to be seen.

6 years ago
Reply

I purposely kept the post brief. Not looking for technical assistance, just assistance with a copy of wiring diagrams.