Any one with insight on how the majors keep the fire rating of the entrance frames with the access doors for the control components of MRL's?



   
Quote
(@ashley)
Joined: 1 second ago
Posts: 0
 
The covers meets the 14 ga. thickness required for a fire rating. The frames had to be relisted to include the openings before they put them in the field. The are not modifying an existing frame so to speak.



   