Hoistway entrance fire rating.

2 Posts
2 Users
0 Reactions
2,130 Views
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643
Topic starter   [#26379]
Any one with insight on how the majors keep the fire rating of the entrance frames with the access doors for the control components of MRL's?



   
Quote
(@ashley)
Reputable Member
Joined: 17 years ago
Posts: 176
 
The covers meets the 14 ga. thickness required for a fire rating. The frames had to be relisted to include the openings before they put them in the field. The are not modifying an existing frame so to speak.



   