W ERL Problem

15 Posts
5 Users
0 Reactions
13 K Views
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
Topic starter   [#6110]
Group of 4 cars, the number one car is stopping at all floors in the up direction. Down is fine. I was getting calls every 20 mins about it. I walked over and took the car out of service, I was in the middle of changing mirco switches on a W escalator on the bottom upthrusts, so I havent got to spend anytime trouble shooting the problem. Car wasnt on emergency s dispatch. 57tt and 45tt were out. 438 was picking and dropping like normal. Ive spent little time working on this equiptment so any pointers would be awesome.

Last edited by sbrmilitia; 03/08/13 01:36 AM.


   
Quote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480
 
438 should only fire for a hall call. See why 34's are picking at every floor in the up direction. It's probably an opposite direction back contact in the slowdown circuit but that's just a guess without looking at prints.

Last edited by E-man; 03/08/13 03:44 AM.


   
ReplyQuote
 Len
(@len)
Estimable Member
Joined: 17 years ago
Posts: 194
 
On that equipment..I think if i remember correctly the 38 relay is your initiate for a stop..might want to look at that circuit...



   
ReplyQuote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480

   
ReplyQuote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480

   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448

   
ReplyQuote
(@uppo72)
Honorable Member
Joined: 17 years ago
Posts: 562
 
This is a good lesson for the new mechanics. Years ago we only really worked on our own equipment(factory) but those days are largely gone(there used to be no poaching policies). So when confronted with new gear i always try correlate the main actions that drive lifts so that you can familiarise yourself with lifts you havent seen before. Safety,direction,door locks,reverser ccts,slowdown,stopping,door action.

Write it down. After time you will remember it.



   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
Topic starter  
Yeah I have some good notes. I also work with a guy who has 30 years in the trade and worked for Westinghouse for a good while. He spent 20 years in a high rise with nothing but DMR and ERL. I cut my teeth on a/b base. I cannot believe how much easier the Otis stuff is to work on then this Westinghouse. I still rather have 100 Dover Composites then any Westinghouse.



   
ReplyQuote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480
 
Composite? Oh how I hate composite. I would rather have 100 ERL's.. Actually, I have about 10 TIV's on my route, I would say screw those generators in a heartbeat and take 100 TIV's.



   
ReplyQuote
 Len
(@len)
Estimable Member
Joined: 17 years ago
Posts: 194
 
The Westinghouse are challenge keeps you thinking..not to crazy about the soldered connections on the relays..makes it a chore to replace..unless you get the Adam upgrades..



   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
Topic starter  
As long as I have a I/O grid that I could see my modules and hyperterm to enter commands, you could do away with the fault log faults are useless, I would take a 100 TIVs any day over any MG car.



   
ReplyQuote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480

   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448

   
ReplyQuote
(@broke-sheave)
Reputable Member
Joined: 17 years ago
Posts: 418

   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448

   
ReplyQuote