1209=Missing NOde (something in comunication)or power filure in LON sometimes has 24v in controller and just 20v in Cab (for LON)
pres OK and Show you a Extra info is a Long number ex.(000100002)
97=ETSL_MISC (check Vane or any error reading the Terminal)(make a new JFL "learn trip")
10-FC_FAULT: is a Emergency Stop (suddenly)
sometimes if open a Interlock at high speed or any Charging Fault in the Drive in TX some time auxiliary contacts from SH contactors
Do you have any info on how to put the car on wild car opp, with doors closed and stop at random flrs, would be awesome!
Dave
for door disable, go to menu found "Special Trip" next KFM tourn in ON
with KFM car run with door disable
press button 1 & 2 to return to Status Disply
in the Status Display
if you press button 1 an 4 at the same time you could make car calls
to return to normal go to Special trip and Turn OFF KFM
""let try to found my manual for extra infos""
and yes Fault 10 has NO extra info 😉