I have a transformer that is reading only 1.3 ohms between h1 & h2 on primary side. The reading increases .1 ohm as I measure between h1 and other taps as expected. My question is, isnt this Reading way too low, indicating a short? Thanks in advance.



   
Quote
(@jimbonj)
Estimable Member
Joined: 17 years ago
Posts: 67

   
ReplyQuote
(@micmerci)
Active Member
Joined: 17 years ago
Posts: 10
Topic starter  
Trips breaker as soon as starter kicks in. Ended up being fault contactor defective. I guess the transformer reading was accurate



   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
Transformers and other windings use Inductive Reactance after the Voltage is applied. The Ohmic Value with no Volatge is inherently low.



   
ReplyQuote
(@danzeitz)
Prominent Member
Joined: 17 years ago
Posts: 672
 
Ive chased a couple of shorts back to a transformer I had forgotten to unhook while looking for the cause of a blown fuse.



   