17/07/2016 4:07 am
I have a transformer that is reading only 1.3 ohms between h1 & h2 on primary side. The reading increases .1 ohm as I measure between h1 and other taps as expected. My question is, isnt this Reading way too low, indicating a short? Thanks in advance.
17/07/2016 7:30 am
Is it burnt ? Are you blowing fuses before it?
Topic starter
17/07/2016 8:17 am
Trips breaker as soon as starter kicks in. Ended up being fault contactor defective. I guess the transformer reading was accurate
17/07/2016 9:19 pm
Transformers and other windings use Inductive Reactance after the Voltage is applied. The Ohmic Value with no Volatge is inherently low.
20/07/2016 3:18 am
Ive chased a couple of shorts back to a transformer I had forgotten to unhook while looking for the cause of a blown fuse.