tac50 fault 109 encoder cross check error

5 Posts
1 Users
0 Reactions
5,725 Views
(@green sleeves)
Joined: 1 second ago
Posts: 0
Topic starter   [#7427]
Been fighting this for a while. Replaced motor and governor encoders and made adjustments to cpf, rpm, rev and trk with either no difference or negative effects. Tried to monitor vel while running but thats really hard to do when you have to wait for it to shut down with that fault. Has a slight vibration leaving the top floor but rails are not tight. Intermittent problem shuts unit down once every couple of days. Any insight would be GREATLY apprecited.



   
Quote
(@Johnny)
Joined: 1 second ago
Posts: 0
 
Have you cleaned the governor optics and bar code reader? The optic reader and bar code are inside the governor mounted to the circumference of the sheave. This compares the speed reference with the encoder.



   
ReplyQuote
(@green sleeves)
Joined: 1 second ago
Posts: 0
Topic starter  
Yep. Done all of that. We did test for and find rope slippage of about 9" and will try a little rope lube to swell the ropes. Also will check balanced load but still kinda stuck.



   
ReplyQuote
 Wolf
(@Wolf)
Joined: 1 second ago
Posts: 0
 
Governor cable could be lose on top of car at the crosby



   
ReplyQuote
(@green sleeves)
Joined: 1 second ago
Posts: 0
Topic starter  
rope lube took care of it.



   