Tac32 cpua replacement procedures

7 Posts
4 Users
0 Reactions
4,265 Views
 Jm21
(@jm21)
Eminent Member
Joined: 17 years ago
Posts: 11
Topic starter   [#38975]
Hello everyone
I'm looking for the procedures to replace the CPU a on a tac32 hydro. I just need the steps on how to download the job files and then upload them on the new CPUA. Any help is appreciated. Thank you

Last edited by Jm21; 02/11/25 02:19 AM.


   
Quote
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359
 
Insert a blank USB memory stick into the USB slot on the CPUA board and enter UDLS in IMS Smart Fast. It show backing up software & then backup complete which will save the generic and job file to the stick. You can then connect the USB stick to a laptop. When it opens, open the TKE folder. Right click and create an update folder. Open the backup folder, and then open the job folder. Right click on the Generic and job file and select Copy. Open the update folder, right click and paste. Insert the memory stick into the replacement CPUA board. Press & hold Reset, then press & hold UDL. Let go off Reset while continuing to press and hold UDL until the LED flashes slow, slow, fast, fast and release UDL. When the upload is complete the controller will reset. Be sure to be on inspection while doing this.



   
ReplyQuote
 Jm21
(@jm21)
Eminent Member
Joined: 17 years ago
Posts: 11

   
ReplyQuote
(@gohana256)
Eminent Member
Joined: 17 years ago
Posts: 29

   
ReplyQuote
 Jm21
(@jm21)
Eminent Member
Joined: 17 years ago
Posts: 11

   
ReplyQuote
(@gohana256)
Eminent Member
Joined: 17 years ago
Posts: 29

   
ReplyQuote
(@suthrn)
Active Member
Joined: 17 years ago
Posts: 7

   
ReplyQuote