About 2 weeks ago I was working on a TAC 20 in Brooklyn, when I hooked up my computer I found faults for memory corruption and what not. Long story short I reloaded the job parameters, but now the security system is NOT working. They have key pads in the hall that, and once the client types in their code allow them to access there floor. I have a feeling that I need to adjust the parameters in the software for the security system, but every time I make a change the elevator will turn off.
Has anyone ever worked on a TAC 20 security system?
Next, when changing security parameters the elevator must be turned off before it takes hold. Each time you change the type, cycle power, then try and test the reader.
Iet me know if you need something more in depth, and I will try and find a TAC 20 nearby to assist.
Very common in our area to field add these, and not everyone has floppy drives anymore so very understandable that the backup .cfg doesn't have them saved. If you are trying to do this without IMS, good luck. May want to call a TKE buddy and bribe him with a coffee...