Elevator Forum

Swift futura...146 ...
 
Notifications
Clear all

Swift futura...146 fault overload

19 Posts
6 Users
0 Reactions
29.6 K Views
(@lizard)
Active Member
Joined: 17 years ago
Posts: 11
Topic starter  
Still to no avail, it went down again an hour later.....the headache continues....

Last edited by lizard; 11/19/15 02:43 AM.


   
ReplyQuote
 jkh
(@jkh)
Prominent Member
Joined: 17 years ago
Posts: 904
 
There is a fault menu on the drive and it does keep a history. Although I am sceptical it's your drive.
Also as vator gator stated the normally closed TH contact is a thermal sensor on the DB resistors. I would like to add there is another item that senses heat that will shut down your elevator. The SPU board has a heat sensitive chip mounted on it.
Are your service calls always come in during peek times of the day? This maybe a bit of a long shot, point a fan at the SPU...

Good luck and please keep us posted.



   
ReplyQuote
(@smitty)
Reputable Member
Joined: 17 years ago
Posts: 220

   
ReplyQuote
(@miltronics)
Eminent Member
Joined: 17 years ago
Posts: 35

   
ReplyQuote
Page 2 / 2
Share:
Scroll to Top