Elevator Forum

Notifications
Clear all

SSC6010

4 Posts
3 Users
0 Reactions
2,790 Views
 Leob
(@leob)
Active Member
Joined: 17 years ago
Posts: 9
Topic starter   [#17308]
Hi,
I've got a 6010 that trips the comparator board and doesn't even move. 1M and the brake picks up. 1,2,3, and 6EA boards have been replaced. Drive was also swapped from a running car. Voltage on the speed comparator was at 6 volts. Any ideas???
Thanks.



   
Quote
 Leob
(@leob)
Active Member
Joined: 17 years ago
Posts: 9

   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
do you have a voltage on the fields? what is the Comparator Board Trip point set at? Are the M switch Contacts good? If you bypass the Comparator will it run?



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
You are getting a pattern to the comparator board but the car is not moving so you have no tach feedback, the error voltage trips the board. Does it run on inspection? If it trips on inspect, jump out the comparator and troubleshoot why the car is not moving. You said the brake picks, assuming it clears completely, do you have voltage on the field? On the armature?



   
ReplyQuote
Share: