anyone have the experience of at the end of run /dropped main contactor. The emergency brake contact picks(eb) ebrake board doesn't output voltage. Roughly around the time of full door open
my inputs for all door locks and safeties go low(led only,still have power on them)
2)machine room sru board that I replaced, unsuccessfully synced(tried several times) cmra,mrb fault and alarm leds flashing, board is not communicating with the cop/ct boards. Went through checking wiring,voltage etc after not receiving a call back from smartrise, installed original Mr sru(plug everything in no changes to dip switches) it went through automatic sync and I can operate the elevator
Original software ver 01.02.64a0 new 01.02.64h0
They all dropped at same time.
As previously stated after the run when main(motor/drive) contactor
And main brake contact drop no demand for movement the EB output from the sru goes hi(which is the emergency brake contact) however there is no voltage output from the ebrake board
Shortly thereafter on the right side of the machine room board the input LEDs for the door locks and safeties all go low for a few seconds (they still have 120vac on them)
Both of those situations aren't normal ebrake picking after a run and the i/o all dropping out at same time with power on them. I have called early a.m. a few times and never received a call back from smartrise