Siemens Starter Fault

5 Posts
3 Users
0 Reactions
4,697 Views
(@elevatorguycny)
Trusted Member
Joined: 17 years ago
Posts: 25
Topic starter   [#21163]
Getting a "Incoming Power Low Line" on the screen. Fault contactor pulls in, then we get that message and it drops out. All legs are reading 480-483 volts. Reading 120v between 1 & 3 on the starter. Waiting on a call back from Siemens but my guess is bad starter?



   
Quote
(@elevatorguycny)
Trusted Member
Joined: 17 years ago
Posts: 25

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@cbass)
Eminent Member
Joined: 17 years ago
Posts: 27
 
Did you measure voltage with a meter or use the Status Menu on the starter? The menu on the starter will tell you what the starter is seeing. If it differs from your meter, something is wrong with your starter. I don't think you can adjust the low voltage clamp on those starters.



   
ReplyQuote
(@elevatorguycny)
Trusted Member
Joined: 17 years ago
Posts: 25

   
ReplyQuote