Hello. Working on a traction LRVF. does any one have fault codes for this. I’m getting a 2647. Car stops in between floors like it lost. Then restarts trip



   
Quote
(@someguy)
Trusted Member
Joined: 17 years ago
Posts: 40

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@someguy)
Trusted Member
Joined: 17 years ago
Posts: 40
 
PM me.

I'd advise you to start backing away from these if you can. We lost a drive a while back, and had a hell of a time getting the drive up and working again. We did everything we could, but the building could not understand what we were up against, and acted like spoiled children. We had been telling them for years that that day would come.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
So after changing the phase relay I am now getting faults

9007 - DRV DECEL TOUT (on normal slow down the drive did not send a signal back that had completed the slow down )

9008 - DRV READY TOUT ( before a run command was giving the drive did not state it was ready to run

And I still get 2647 J relay intermittently also

My main line power seems good I think it’s the drive. Anybody have these symptoms before ?

Last edited by Jluff; 06/11/22 02:42 PM.


   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
These are all the faults I’m getting. We changed the J relay. Had drive tested and drive power supply replaced. Still getting these codes. Power is good to my drive. But it’s intermittent. I can’t catch it with my meter in the machine room .. I think there could be multiple problems still. Changing selector board and guides soon. Board is on back order. But I think there could be building power problems also. There is a big Otis elevator transformer in a big blue box .. I think it takes 3 phase 4 wires and converts it to 220v 3 phase 3 wires .. but this seems ok when I test power

2642 - floor position failure in flight or while in door zone.
2647 - phase loss - J relay detected open phase in power supply
2005- car not available mcss reports car not available to answer calls
9007 - DRV DECEL TOUT (on normal slow down the drive did not send a signal back that had completed the slow down )

Last edited by Jluff; 07/13/22 04:38 PM.


   