I have a 1993 2,3 Otis HOCL microcomputer elevator. Problem is when fire service phase 1 is activated, elevator goes to lower level instead of main floor with fire key switch, 2 stop.
Is there a jumper somewhere that has to be moved?



   
Quote
 jkh
(@jkh)
Prominent Member
Joined: 17 years ago
Posts: 904

   
ReplyQuote
 Boa
(@boa)
Estimable Member
Joined: 17 years ago
Posts: 141
 
I have prints for a 2,3 HOCL microcomputer, LRV4, dwg #2-1s7910ag if it helps. For a 2 stop I would make sure the detectors are wired properly. If yours is another version let me know I should have info



   