OTIS GEN 2

8 Posts
1 Users
0 Reactions
14.5 K Views
(@chicago)
Joined: 1 second ago
Posts: 0
Topic starter   [#19241]
Hello Guys,
Otis Gen 2 problem. Elevator runs on mr inspection, runs on car top, runs on fire service. Will not run on normal operation.
Testing guys at site day before, everything ok when they left?
Saw G003 fault, now cleared.
Won't take calls.
Any ideas



   
Quote
(@NewMech)
Joined: 1 second ago
Posts: 0
 
CHCS switch?
DDOS switch?
Do you have a DLF displayed on your car monitor?



   
ReplyQuote
(@vader potater)
Joined: 1 second ago
Posts: 0
 
When was the unit installed? You may want to check the controller backup batteries at the bottom of the controller. If they are starting to get weak it can cause similar issues. They need to be replaced I believe every 5 years or so.



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
If it is the batteries OCSS will be NAV and there will be a current fault that won't clear, don't remember which. Don't rule out the batteries because they read the correct voltage!



   
ReplyQuote
(@chicago)
Joined: 1 second ago
Posts: 0
Topic starter  
Problem was flat belt sensor.
Time to change cables(belts).
Turned off sensor, car ran.



   
ReplyQuote
(@beaupeep)
Joined: 1 second ago
Posts: 0
 
Which key unlocks panel that gets to controller?



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
 
I think it's a UTB or UTC to unlock panel. How do u navigate thru the menus to get to the belt sensor with the service tool?



   
ReplyQuote
(@chicago)
Joined: 1 second ago
Posts: 0
Topic starter  
You need to hook up fast tool too "installation" port then proceed to flat cable ohm sensor.I left my notes on how to navigate on job.



   
ReplyQuote