Otis 211 Phase 2, write protect

4 Posts
1 Users
0 Reactions
1,756 Views
(@Pititi)
Joined: 1 second ago
Posts: 0
Topic starter   [#40117]
Thanks in advance. Otis 211 Phase 2, it is in fault fslr, the selector signals are good in the I/O board, i need to change some parameters but when i reset the controller the parameters go to preview number.
No Service Tool can talk with the elevator ( i dont know why) i have tested four diferent Service Tool in both elevators.
So, how to put in off the write protection from the controller, i suppose it is what avoid to change the parameters.



   
Quote
(@tayto)
Joined: 1 second ago
Posts: 0
 
copy parameter chip onto a new chip. software version is too old, need AAJ or newer.



   
ReplyQuote
(@Pititi)
Joined: 1 second ago
Posts: 0
Topic starter  
The version is AAI, Where can i find the newer version? it is suppose i should contact to OTIS, Correct?



   
ReplyQuote
(@Pititi)
Joined: 1 second ago
Posts: 0
Topic starter  
Where connect the service tool in otis 211 phase 2? I see only Diagnostic connector and the ST doesn’t work there. Others models have Diagnostic and ST connector.
If I connect the ST in Diagnostic I get the same result in any model, so Diagnistic isn’t the correct one for the ST.
Does 211 phase 2 use ST?



   
ReplyQuote