Elevator Forum

Otis 211 Phase 2, w...
 
Notifications
Clear all

Otis 211 Phase 2, write protect

4 Posts
2 Users
0 Reactions
1,827 Views
(@pititi)
Eminent Member
Joined: 17 years ago
Posts: 15
Topic starter   [#40117]
Thanks in advance. Otis 211 Phase 2, it is in fault fslr, the selector signals are good in the I/O board, i need to change some parameters but when i reset the controller the parameters go to preview number.
No Service Tool can talk with the elevator ( i dont know why) i have tested four diferent Service Tool in both elevators.
So, how to put in off the write protection from the controller, i suppose it is what avoid to change the parameters.



   
Quote
(@tayto)
Trusted Member
Joined: 17 years ago
Posts: 70

   
ReplyQuote
(@pititi)
Eminent Member
Joined: 17 years ago
Posts: 15
Topic starter  
The version is AAI, Where can i find the newer version? it is suppose i should contact to OTIS, Correct?



   
ReplyQuote
(@pititi)
Eminent Member
Joined: 17 years ago
Posts: 15
Topic starter  
Where connect the service tool in otis 211 phase 2? I see only Diagnostic connector and the ST doesn’t work there. Others models have Diagnostic and ST connector.
If I connect the ST in Diagnostic I get the same result in any model, so Diagnistic isn’t the correct one for the ST.
Does 211 phase 2 use ST?



   
ReplyQuote
Share:
Scroll to Top