Having an issue with this unit. Keeps going down every other day. So far has gone down 3 times since 11/25/20. Faults have been ULFB. SHD.
DMFB. SHD.
UMFB SHD.
All of them reset easily and it runs after. Any ideas what I should be looking to or for for the possible issue here? My first impression is these are valve coil/valve related issues. But I have taken apart and cleaned the screens and stem seats. No change in observable operation. Any thoughts anyone?



   
Quote
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
It means the valve output was turned on but the feedback input didn’t see the voltage or the feedback input saw a voltage when the valve output was not turned on. For it to happen with 3 of the 4 valves is weird. Only thing in common with all the valves is the safety string. Maybe a flakey contact in there somewhere or a loose connection.



   
ReplyQuote
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143
Topic starter  
Maddening... Where do I look to fix this then? Replace valve coils? Replace selector board for possibly sending erroneous signals?



   
ReplyQuote
 M2RE
(@m2re)
Estimable Member
Joined: 17 years ago
Posts: 82

   
ReplyQuote
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143
Topic starter  
Not routinely. It did do a dance when the oil was cold one time, settled and releveled and shot through and leveled down. Only saw that once with cold oil and it didn't shut it down.



   
ReplyQuote
 M2RE
(@m2re)
Estimable Member
Joined: 17 years ago
Posts: 82
 
Make sure to isolate hydraulic leaks, via doing a sit test. I don’t know but maybe its going down mechanically and causing the lift to fault out.



   
ReplyQuote
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143
Topic starter  
According to a 418 page manual I read there are 2 possibilities for this fault. 1. Directional limit tripped while the valve coil is picked/energized. 2. Mother board component u78 is bad and generating false signal.. So we have gone through all the HW switches and adjusted the UP final further away from the landing by 1/2" incase the unit it intermittently leveling through or shooting through the floor.. We will see how it goes.



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
The problem with that is you have had both up and down valve faults so 1 directional limit switch can’t account for all of your faults. I suspect the board.



   
ReplyQuote
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143
Topic starter  
Yeah... That was my concern too. But to rule it out we adjusted it any way. But it's down again today. So not sure how we are gonna proceed now..



   
ReplyQuote
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143
Topic starter  
The valve seems pretty solid. Not releveling a lot. But these faults all say Valve feedback.. Scratching my head on this one..



   
ReplyQuote
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143
Topic starter  
I guess we will try replacing the selector board and rule that out. Possible false signals being generated by the selector..



   
ReplyQuote
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143
Topic starter  
Replaced selector board. And it was down again today. So today we replaced the stems/seats on the maxton valve to rule out that section of the valve at least... We will see tomorrow.



   
ReplyQuote
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143
Topic starter  
It appears that replacing the stems and seats on the maxton valve has repaired the issue. Original issue being a SHD status with one of the following faults. ULFB UMFB DMFB DLFB.



   