motion control MLT FAULT!!!

9 Posts
1 Users
0 Reactions
15.6 K Views
 mbke
(@mbke)
Joined: 1 second ago
Posts: 0
Topic starter   [#4236]
Keep getting MLT faults on motion.change aux on m contactor . brushes good brake is good. hc-acif board is good.what next????



   
Quote
(@Johnny)
Joined: 1 second ago
Posts: 0
 
What kind of drive do you have? Generator? DC motor? VVVF? SCR? What is happening when it goes into fault? Stalling at the floor? Not taking off? Type of elevator, etc?



   
ReplyQuote
(@E-man)
Joined: 1 second ago
Posts: 0
 
If it has a drive, it could be as simple as a drive parameter being wrong. We had an MCE Engineer come to teach a class at our office and I suggested for the on the job portion of the class that we go to that job with the MLT prob (since it had been going on for a while and I inherited the problem). We went out ther and he found it pretty quick...



   
ReplyQuote
 Vic
(@Vic)
Joined: 1 second ago
Posts: 0
 
What type of MCE? IMC DC? VVC PG? M4000? Should we guess?

When you present a question, try to include salient details.

We love to gab, but gotta have a starting point!!

😆



   
ReplyQuote
(@selfproclaimed)
Joined: 1 second ago
Posts: 0
 
The contactors used by MCE seem to be undersized and only last for a year or two. Start by checking the M contactor and the brake contactor with aux contacts. Ohm them out and see how much resistance you have on each pole. As stated above...What type MCE would narrow it down.



   
ReplyQuote
 mbke
(@mbke)
Joined: 1 second ago
Posts: 0
Topic starter  
its a magnatech drive . no gene westinghouse machines



   
ReplyQuote
 mbke
(@mbke)
Joined: 1 second ago
Posts: 0
Topic starter  
cool thanks



   
ReplyQuote
 mbke
(@mbke)
Joined: 1 second ago
Posts: 0
Topic starter  
its vvc



   
ReplyQuote
(@Smitty)
Joined: 1 second ago
Posts: 0
 
MLT faults can be caused by a lot of stuff. MCE starter auxiliaries
are crap if these are the kind you can change one at a time. Typically you will have a few NO contacts monitoring drive contractor on as well as a few NC which monitor that the M switch dropped out. They tend to be junk.



   
ReplyQuote