Elevator Forum

Notifications
Clear all

Montgomery HH2

5 Posts
3 Users
0 Reactions
3,296 Views
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359
Topic starter   [#26882]
I've got a 2-stop old Hydro unit that is floor level with the doors open. It will run up/down on INSP, but will not run up/down on auto.

Please see the attached prints.

Attachments
IMG_02141001.jpg (304 KB, 59 downloads)
IMG_02151001.jpg (221.06 KB, 44 downloads)



   
Quote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798

   
ReplyQuote
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359

   
ReplyQuote
(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635
 
Did you get it figured out today?
———————————————————-
Status of DOP, DO and PC in controller?
Safe Edge contact?
Door Board test/manual switch set incorrectly?
Operator Relays?
Stuck DOB?
Just a few ideas....



   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
The print is hard to read, but it looks like you have to pick UDX to drop the DO relay. The UDX relay is picked with a direction, either up or dn. The common link in the direction circuit is, from what I can make out either LR or IR relay. take a close look at those associated contacts and relays. You should come up with a solution. Good Luck.



   