If you have a 100amp service to your disconnect and the new controller manufacturer is recommending 45 amp. What size should the disconnect fuses be ?



   
Quote
(@NOTIME)
Joined: 1 second ago
Posts: 0
 

Last edited by NOTIME; 02/19/24 11:20 PM.


   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
Thank you.



   
ReplyQuote
(@Montana)
Joined: 1 second ago
Posts: 0
 
Usually the controller manufacturer will list the mainline disconnect size on the print. In your case they are probably calling out a 45 amp disconnect so 45 amp fuses. They should of calculated this load off of your survey of the equipment being modded. What equipment and controller are you going with?



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
Alpha Controller
Canton Power Unit.
480v
25 HP motor.
I think FLA was 33.9
75fpm

Last edited by Jluff; 02/20/24 05:49 PM.


   