If you have a 100amp service to your disconnect and the new controller manufacturer is recommending 45 amp. What size should the disconnect fuses be ?



   
Quote
(@notime)
Reputable Member
Joined: 17 years ago
Posts: 197

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@montana)
Honorable Member
Joined: 17 years ago
Posts: 515
 
Usually the controller manufacturer will list the mainline disconnect size on the print. In your case they are probably calling out a 45 amp disconnect so 45 amp fuses. They should of calculated this load off of your survey of the equipment being modded. What equipment and controller are you going with?



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
Alpha Controller
Canton Power Unit.
480v
25 HP motor.
I think FLA was 33.9
75fpm