Replaced pumping unit. Now when I turn to automatic it immediately gets the low oil timer. I’ve adjusted the pot, replaced the card and card rack Any help in why this might be would be helpful



   
Quote
(@EElevator)
Joined: 1 second ago
Posts: 0
 
Was the low timer a float switch on the old tank unit?

Code allows for a timer or switch for low oil protection



   
ReplyQuote
(@john jay)
Joined: 1 second ago
Posts: 0
 
Sounds like PT input is high. That is the low oil input.



   
ReplyQuote
(@danzeitz)
Joined: 1 second ago
Posts: 0
 
did you replace starter with pump unit? Maybe to a soft start?



   
ReplyQuote
(@stanklerbin)
Joined: 1 second ago
Posts: 0
 
HA on relay board starts the time for low oil



   
ReplyQuote
(@stanklerbin)
Joined: 1 second ago
Posts: 0
 
My mistake.
UA relay picks and starts run times.

Apologies.



   
ReplyQuote
(@Stall Protection)
Joined: 1 second ago
Posts: 0
 
Bump for visibility.

I'm in the same situation.



   
ReplyQuote
(@Stall Protection)
Joined: 1 second ago
Posts: 0
 
My problem ended up being the TUS input. Lost a jumper with the removal of the old power unit.



   
ReplyQuote