Happy Holidays Group,
I wonder if I could pick your brains on a Miprom 21?
6 stops in line, 350 FPM geared AC.
Elevator shut down a few inches from floor, no hard faults or soft faults. All led's indicate elevator is ready to run upon demand, safety circuit is good, relay status is correct but no calls can be registered. Hall buttons light and go out as soon as button is released. Car will not operate on inspection.

When service tool is connected there is no communication. Tries to log on then displays "turn tool off".

Any thoughts would be appreciated, Thank You



   
Quote
(@galaxy)
Eminent Member
Joined: 17 years ago
Posts: 34

   
ReplyQuote
(@philly)
Reputable Member
Joined: 17 years ago
Posts: 256

   
ReplyQuote
(@christycollett)
Honorable Member
Joined: 17 years ago
Posts: 420

   
ReplyQuote
(@christycollett)
Honorable Member
Joined: 17 years ago
Posts: 420
Topic starter  
Update on the Miprom 21.

As stated all I/O 's and voltages looked fine and no faults were displayed. I was incorrect on the registering of hall calls as they could be registered and would remain registered.

The elevator was about 3/4" below bottom landing. Not on directional.
Mechanic reset main line power but problem remained. He then removed all Miprom 21 boards from the card rack then reseated them back into slot. He then removed all ribbon cable plugs and reseated them. Car has been running since and tool logs on no problem.



   
ReplyQuote
(@philly)
Reputable Member
Joined: 17 years ago
Posts: 256
 
I'd be expecting a repeat call. Sounds like an input card (or PIO) about to take a dump. Look for a dim led next time and check for less than 120vac on that card. Usually around 77 as it's the same resistor that fails over time. Seen it a dozen times.

Last edited by Philly; 12/28/12 03:06 PM.


   
ReplyQuote
 MAYU
(@mayu)
New Member
Joined: 17 years ago
Posts: 1
 
I am facing same issue dear Philly or any respected menbers Kindly Give more detail on your idea,

Last edited by MAYU; 05/02/19 06:30 AM.


   
ReplyQuote
(@snkrhead)
Estimable Member
Joined: 17 years ago
Posts: 77
 
Having a issue with a duplex latching ghost hall calls
Seen it one time
Customer reports that the 1st floor hall call will just lath he bu itself and elevators start acting crazy.
They always reset the power on both cars before I get ther any suggestions will be very helpful!



   
ReplyQuote