miprom 21 vp13 fault

3 Posts
2 Users
0 Reactions
3,415 Views
(@vatorgator)
Honorable Member
Joined: 17 years ago
Posts: 432
Topic starter   [#15728]
have a unit that is faulting out on a vp13, motor field feedback fault. started a couple months ago, route guy reset, and it ran another month, another reset, now it is starting to do it once a week or so. i reseated connections in drive for the motor field circuits, checked connections to mf, also checked reference current with feedback current, and while i was there, they were right on. sure its coming back, just wanted to get your ideas on what to replace first, feedback board ? etc, just wondering if anyone has had this before. thanks



   
Quote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
Usually this is caused by the field firing board. It is behind the field feedback board. It has 4 120 ohm resisters, 2 per side in parallel. these should measure around 60 to 65 ohms. they get hot and start flaking out.



   
ReplyQuote