Miprom 21 -Alt Profile

4 Posts
3 Users
0 Reactions
3,396 Views
(@redexit)
Eminent Member
Joined: 17 years ago
Posts: 13

   
Quote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
Have you checked your EP input. The alt profile is used to let under-sized Backup Generators run the Elevators at a slower,lower speed and Amperage draw. When the unit is on Backup power the alt profile is used, if the parameter for alt profile is set up. You can access the parameter with the service tool.



   
ReplyQuote
(@redexit)
Eminent Member
Joined: 17 years ago
Posts: 13
Topic starter  
John Jay..Thank you for your fast response. and yes you were 100% correct. I didn't have my books with me at the time, but I verified your feed back. The EP input was hi( Emergency Power); however, the input L.E.D. on the card was out so I didn't see at first until I verified with my meter. I had not seen this one before...I sincerely appreciate you help.