Miprom 21 Allen Bradley Dc drive

5 Posts
3 Users
0 Reactions
5,875 Views
(@cucuvator)
Estimable Member
Joined: 17 years ago
Posts: 81
Topic starter   [#16826]
Hi everyone,fault 11 every morning,Relay pilot leds F1,F2,F8.
I got the fault code manual but missing the Dc drive page.

Thanks



   
Quote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
This fault indicates a field loss. I would start with checking for loose connections in the Field Circuit.Why you are only getting it in the morning is unusual. Check the field Parameters. Rated Field Current should reflect the Jumper on the Field Feedback Board.



   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
This fault indicates a field loss. I would start with checking for loose connections in the Field Circuit.Why you are only getting it in the morning is unusual. Check the field Parameters. Rated Field Current should reflect the Jumper on the Field Feedback Board.



   