Elevator Forum

MCE- leveling senso...
 
Notifications
Clear all

MCE- leveling sensor failure- fault

6 Posts
1 Users
0 Reactions
5,300 Views
(@Jspee508)
Joined: 1 second ago
Posts: 0
Topic starter   [#38353]
Hi. I have an MCE VFMC-1000, with an LS-qute reader.
I keep getting “leveling sensor failure-off position”. Then it shuts down on MTL. I Reset controller and will run until it randomly happens again, sometimes 30 mins later, sometimes two days later . Its always floor level, i dont know if it happens coming into the floor or when its idle. No one has ever been in it when it happens. I have replaced the tape reader unit. It ran for a day and happened all over again. It’s usually the same floor (6) but not always.
Magnets look ok visually. The elevator gets alot of use in an elderly 12 floor building



   
Quote
(@Montana)
Joined: 1 second ago
Posts: 0
 
MCE tech support 916-463-9200



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
Use the MLT data trap if if the software is new enough. You can see the state of the IOs when it happened. Question though, how are you seeing the level sensor failure error if it’s on MLT when you get there?



   
ReplyQuote
(@EElevator)
Joined: 1 second ago
Posts: 0
 
The ac interface boards are great for intermittent problems too. Check those, and at a minimum replace the relays on them



   
ReplyQuote
(@Jspee508)
Joined: 1 second ago
Posts: 0
Topic starter  
The lcd screen displays “ leveling sensor failure”



   
ReplyQuote
(@Jspee508)
Joined: 1 second ago
Posts: 0
Topic starter  
Thank you , i will check



   
ReplyQuote
Share:
Scroll to Top