Got an Otis LRV on the springs. Can’t run up. DR relay is picked. In ground jack. Sent relay and controller board off for repair. Got them back from repair, still nothing. Voltages and fuses are good. Any suggestions on what next?



   
Quote
(@flyballgov)
Estimable Member
Joined: 17 years ago
Posts: 69
 
If you ground the pm and umv contacts will the car move up? Need to check your 9vdc doesn't have any ac current on it



   
ReplyQuote
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359
Topic starter  
I was able to get it moving energizing the up coil and pushing in on the wye contactor but still won't run on automatic or inspection. I've also checked the limit switches and they are all good.



   
ReplyQuote
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359
Topic starter  
I was able to get it moving energizing the up coil and pushing in on the wye contactor but still won't run on automatic or inspection. I've also checked the limit switches and they are all good.



   
ReplyQuote
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359

   
ReplyQuote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473

   
ReplyQuote
(@alto101)
Trusted Member
Joined: 17 years ago
Posts: 39
 
The controllers are shitty to work on. I don’t take them on unless the client is ready to rip it out and do a mod. No help to your situation besides the simple truth. Waste too much time and the clients money. The tanks can usually stay .



   
ReplyQuote
(@flyballgov)
Estimable Member
Joined: 17 years ago
Posts: 69
 
If you have good voltage on A1 of the PM coil and you ground A2 on PM and it'll pull in then you have a processor issue



   