13/02/2025 7:04 pm
Good morning everybody, almost Friday. So i replaced a door board on a thyssenkrupp LD 03 door operator on a tac32 mrl hydro. I thought it was plug n play but not the case. If i hot the MDo or Mdc buttons the door jerks ridiculously hard but does not move smoothly.
Is there any procedures im missing to program the board?
Any help appreciated 👍
Is there any procedures im missing to program the board?
Any help appreciated 👍
14/02/2025 4:53 am
The board needs to be programmed manually or by uploading a profile to the board through IMS.
19/02/2025 5:25 am
Do you have a UIT for the door board or IMS ? Be careful if it set wrong you could damage more. As set to ac or dc motor