Kone resolve 188 fault any suggestion

10 Posts
5 Users
0 Reactions
15.6 K Views
(@ratman1313)
Eminent Member
Joined: 17 years ago
Posts: 21

   
Quote
 E311
(@e311)
Reputable Member
Joined: 17 years ago
Posts: 363

   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
can be caused by a touchy switch in the rope gripper, make sure the gripper latch's correctly when it energizes.sometimes a power glitch causes it. the first thing the controller sees is the gripper circut drop,actually anything in the safety circut will drop the gripper, the control may be seeing the gripper first.



   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
when you press the acum reset on the adon board does the gripper pick? the fault comes from the led 182 failing to go high or led 181 stayed high instead of going low. the relay on the adon board k464.2 and 464.1 could also be failing intermittently. the early adon boards were nortoriously touchy animals.



   
ReplyQuote
(@ratman1313)
Eminent Member
Joined: 17 years ago
Posts: 21

   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
if you have access to another adon , change it out. a lot of intermittent problems are from the early adon boards.you can't replace the relays on those, you have to replace the the whole board.with problems like this you have to start guessing and eliminating things one at a time.by the way what is the fault log reading.



   
ReplyQuote
(@ratman1313)
Eminent Member
Joined: 17 years ago
Posts: 21

   
ReplyQuote
(@oleeightball)
Trusted Member
Joined: 17 years ago
Posts: 65

   
ReplyQuote
(@ratman1313)
Eminent Member
Joined: 17 years ago
Posts: 21

   
ReplyQuote
(@philly)
Reputable Member
Joined: 17 years ago
Posts: 256

   
ReplyQuote
Share:
Scroll to Top