kone monospace

8 Posts
1 Users
0 Reactions
12.3 K Views
(@denzelevator79)
Joined: 1 second ago
Posts: 0
Topic starter   [#6948]
hello all

i have a kone monospace working on and a keep getting missing 61u,i change the 61u and still getting the same problem,i change the board on top of the lift and still getting the same problem,any input



   
Quote
(@Dmhughes)
Joined: 1 second ago
Posts: 0
 
Hi,
Is it missing all the time or every now and then? If so have you got too much play in top shoes, and did you do a shaft setup?



   
ReplyQuote
(@denzelevator79)
Joined: 1 second ago
Posts: 0
Topic starter  
it misses it all the time and we hve adjusted the switch as close as possible to the magnet



   
ReplyQuote
(@john jay)
Joined: 1 second ago
Posts: 0
 
the magnet could be upside down.



   
ReplyQuote
(@denzelevator79)
Joined: 1 second ago
Posts: 0
Topic starter  
the 61u/61n magnets can turn in any direction unlike the 77u/77n so its something else



   
ReplyQuote
(@Dmhughes)
Joined: 1 second ago
Posts: 0
 
Is this after a shat setup, and have you done a lon download after changing boards? & Are you getting any other fault codes, also what's the distance between the 61u & 61n it should be 128/130mm centres, believe it or not I've had one that was causing havoc with 61 switches & it was down to a faulty tacho (strange)



   
ReplyQuote
(@bk2fla)
Joined: 1 second ago
Posts: 0
 
sounds like you need to do adon learn and lon download



   
ReplyQuote
(@aquadag)
Joined: 1 second ago
Posts: 0
 
bad adon possibly



   
ReplyQuote