Elevator Forum

Kone KCM831 E0108 e...
 
Notifications
Clear all

Kone KCM831 E0108 error

10 Posts
1 Users
0 Reactions
14.7 K Views
(@kenelev)
Joined: 1 second ago
Posts: 0
Topic starter   [#23186]
Hi Guys:
Got error code 0108
Kone KCM831 with V3F16L drive
When try to run down on inspection, elevator drift up and shutdown.
Any idea can help.
Thanks,
Ken



   
Quote
(@john jay)
Joined: 1 second ago
Posts: 0
 
the fault code says it is a Tach error, or a load balance error.



   
ReplyQuote
(@Thomass)
Joined: 1 second ago
Posts: 0
 
Strip and clean out the Tacho then double check load weigher is calibrated (menu 5 submenu 1 should read close to 0 empty car mid shaft. Number displayed is % of load).



   
ReplyQuote
(@kenelev)
Joined: 1 second ago
Posts: 0
Topic starter  
Thanks guys,
Will check out the tach tomorrow.
As for the load weighter, I cannot run car down because every time try to run down. The elevator drift up and shutdown.
Is there any way to run the car by disable the load weighter?
Or what is the % of the load shoulf be when can @ top ?
Thanks,
Ken



   
ReplyQuote
(@lowoil)
Joined: 1 second ago
Posts: 0
 
I think u can set 5-1 to 50% for construction if i remember



   
ReplyQuote
(@kenelev)
Joined: 1 second ago
Posts: 0
Topic starter  
Thank you guys, is anybody have a copy of setup guide?
Thanks,
Ken



   
ReplyQuote
(@olugbemileke)
Joined: 1 second ago
Posts: 0
 
Any Update @Kenelev, I have a similar problem.
By Tacho, do You mean the Encoder?



   
ReplyQuote
(@Adamabm)
Joined: 1 second ago
Posts: 0
 
Im having the same issue! Were you ever able to figure it out?



   
ReplyQuote
(@Jadam)
Joined: 1 second ago
Posts: 0
 
Clean the encoder, adjust the load weight 50% and 0% top and button shaft.

After that a new shaft setup is a good idear 🙂



   
ReplyQuote
(@irfan)
Joined: 1 second ago
Posts: 0
 
Look like you have broken DCBL board.



   
ReplyQuote
Share: