Topic starter
28/10/2012 1:50 pm
Today i did a stop ring pressure test on a kone kcm 831
for a state inspector. after this test was performed
the car stops on 77u magnet instantly.
I figured it needed a new learn run so i invoked the learn run
menu 5 2 1 and the car runs up to 77u, stops and gives 117
error. multiple attemps same result. also on inspect car runs
for literally 1 second in up direction.
Anyone else experience this?
Any help would be greatly apreciated...
for a state inspector. after this test was performed
the car stops on 77u magnet instantly.
I figured it needed a new learn run so i invoked the learn run
menu 5 2 1 and the car runs up to 77u, stops and gives 117
error. multiple attemps same result. also on inspect car runs
for literally 1 second in up direction.
Anyone else experience this?
Any help would be greatly apreciated...
Topic starter
01/11/2012 6:57 am
Just thought I would leave the findings, in case
anyone else gets this. While using the buffer test
button on cpu40 card it takes 77u,77n out of play to
run to the stop ring. (normal deceleration switches)
The LCEDRV board was registering 77u and 77n active
simultaniously, checked out bar reader, wiring all tested fine.
the cure was to do a complete setup on the LCEDRV board.
after the problem was cured i made both 77u,77n active using
magnets on the bar reader and it faulted this time with the
correct error code (154). it didn't give correct fault number
after using buffer test.
anyone else gets this. While using the buffer test
button on cpu40 card it takes 77u,77n out of play to
run to the stop ring. (normal deceleration switches)
The LCEDRV board was registering 77u and 77n active
simultaniously, checked out bar reader, wiring all tested fine.
the cure was to do a complete setup on the LCEDRV board.
after the problem was cured i made both 77u,77n active using
magnets on the bar reader and it faulted this time with the
correct error code (154). it didn't give correct fault number
after using buffer test.