I have a bank of Minispaces that, during peak traffic, still reportedly stop for hall calls despite being fully loaded. I've dug through the parameter sheet and haven't found anywhere to set a load weigher threshold to bypass hall calls. Am I missing something? This seems like pretty basic functionality, since I have old Haughton, Otis, and Dover relay logic controllers that will bypass hall calls in a heavy load condition.
22/07/2014 3:27 am
menu #1-70, gives you a percentage of a full load adjustment. It will bypass hall calls at that percentage. It doesn't affect LW percentage adjustment.
Topic starter
22/07/2014 7:42 pm
Thank you. I did in fact miss it when I read over the parameter list.