i am working on a kone elevator and keep getting fault 0081
i have replaced the 61u/61n and 30 switches and also makes adjustment.
still getting the fault
this fault started after a power outages any suggestion
i have replaced the 61u/61n and 30 switches and also makes adjustment.
still getting the fault
this fault started after a power outages any suggestion
29/06/2026 9:31 am
Did you do a new shaft setup after replacing and making your adjustments? How many magnets are stacked? What distance do you have it set up to? Ropes lubricated?
Topic starter
29/06/2026 10:37 am
Thank you very much for your response.
it was actually a faulty advance door opening circuit board,
so I turned off the parameter until the board is replace