Topic starter
13/02/2024 9:06 am
Working on a kdl16
We got fault 0108 .we check and found encoder wheel defective.
Replace the wheel know We getting fault 0102.
We had to remove the weights to carry the lift below the top rloor
We got fault 0108 .we check and found encoder wheel defective.
Replace the wheel know We getting fault 0102.
We had to remove the weights to carry the lift below the top rloor
13/02/2024 7:13 pm
What is the sub code of 0102?
Topic starter
13/02/2024 11:43 pm
The subcode I am getting is 2002
Topic starter
14/02/2024 12:23 am
Fault 0102
Subcode 2002
That is the only fault coming up
Subcode 2002
That is the only fault coming up
14/02/2024 3:06 am
Drive DC over current fault
Measured drive DC current too high.
Wrong elevator parameters
Mechanical problem hindering movement
Broken or disconnected LWD feedback.
14/02/2024 3:07 am
Check your load weigher 5-1
Topic starter
15/02/2024 11:20 pm
The load menú 5 1 is at 0%
Menú 6 1=50
Menú 6 2=.5
Menú 6 3=1ms
Menu6 4=400
Menú 6 6=400
Menú 6 7=2
Menú 6 10=50
Menú 6 11=1000
Menú 6 1=50
Menú 6 2=.5
Menú 6 3=1ms
Menu6 4=400
Menú 6 6=400
Menú 6 7=2
Menú 6 10=50
Menú 6 11=1000
The liftcapacity is 630kg
Every time I change it and try to move the lift it goes back to 400
Topic starter
15/02/2024 11:22 pm
Once change 6. 4. to 630kg it goes back to 400 kg
16/02/2024 12:37 am
You need to unlock the parameters I believe, 6-95 needs to be 0
Topic starter
16/02/2024 2:49 am
Ok thanks much
I will check
I will check
17/02/2024 2:31 am
in meanwhile check the motor cable termination at both end.
17/02/2024 2:32 am
Also, don't forget that you have to save Drive Parameter before reset.
change 6-99 to 1 for save.
Topic starter
17/02/2024 10:08 am
Ok thank you !
Topic starter
21/02/2024 4:02 am
Good day all
So I got peogrammed all drive parameters.
I checked motor connection on both ends.
I actually replace the drive but same fault 0102.
Subcode 2002.
I was thinking of the load weighing device base on the subcode.
Can it be bypass
Topic starter
21/02/2024 4:03 am
It is the strain Guage type connected to the ropes