KCM Hydro 831

5 Posts
1 Users
0 Reactions
5,066 Views
(@Elev^te79)
Joined: 1 second ago
Posts: 0
Topic starter   [#9935]
Having an intermittent problem with the elevator running in the up direction on full speed. Coils on the valve checked out good, (4 coils) . K1 relay ringed out good, even get the high speed light on the DRV board but it still runs up like it was on access. I refered to print 800767E04. Any one had this ? Only in the up direction, 2 stops and happens intermittent .



   
Quote
(@Kone D)
Joined: 1 second ago
Posts: 0
 
Valve type? Dirt screen maybe?
Check switch or magnet.
Hoistway learn.
Bad board maybe.



   
ReplyQuote
(@Elev^te79)
Joined: 1 second ago
Posts: 0
Topic starter  
Maxton UC4 valve. Haven't done an acel/dcel learn yet nor have I done a hoistway learn. That's next, after that my only guess is a bad DRV board.



   
ReplyQuote
(@Elev^te79)
Joined: 1 second ago
Posts: 0
Topic starter  
Nevermind , bad 136 switch in the hoistway.



   
ReplyQuote
(@Kone D)
Joined: 1 second ago
Posts: 0
 
Cool



   
ReplyQuote